The Bypass Valve installed at the far point of the Loop between Supply and Return Lines, maintains chilled flow throughout the system when there is no immediate cooling demand. Based on a pressure differential generated when flow stops due to no individual demand, the valve opens and flow is restored. When any demand occurs the pressure differential will drop and the Bypass valve closes.
This valve maintains a safe operating temperature and pressure of the network.
------------------------------
Mike Brown
Cantara Wine & Spirits, Flat Fish Brewing
Camarillo CA
------------------------------
Original Message:
Sent: 06-01-2023 10:19
From: Michael Smith
Subject: glycol piping layout
Ashton: (or anyone else who cares to chime in)
can you elaborate on the purpose and specifics of the pressure bypass valve?
I understand the thought process of keeping the entire loop cold so that when you cycle on a tank its immediately hit with a consistent temp. but is it necessary considering the worst case is they are hit with ambient glycol for a short time only? I also cant help but figure by having this valve in place you are using more energy just cooling the rafters.
I am not against the idea but curious if it would be worth the effort and cost to install.
any idea what they actually are? is it electronic?
------------------------------
Michael Smith
Head Brewer
Eel River Brewing Co.
Fortuna, CA
Original Message:
Sent: 05-23-2023 09:05
From: Ashton Lewis
Subject: glycol piping layout
It's hard to provide much input based on your proposed routing. A few things you may want to do are:
1) Install a back pressure control valve between the supply header and the return header so that glycol is constantly flowing when there is no demand from your demand points.
2) Install a circuit setter on each tank so you can individually set your flows based on pressure drop. Those valves are especially beneficial when you have several tank sizes made by different manufacturers in the same cellar.
3) If your header pressure is constant and you have sufficient flow throughout the system where demand points upstream do not rob flow from downstream demand points, it should not matter where heat exchangers and other types of devices are tied into the system.
4) Find a local mechanical engineer to look over your piping isometrics before installing the system. You guys have been around for a long time and probably have some customer friends in the trade. Ask them to charge you for a few hours of review time. The few hours of engineering review is definitely worth the investment.
Cheers,
Ashton
------------------------------
Ashton Lewis
Manager of Training and Technical Support
BSG Craftbrewing
MBAA District Great Plains, Technical Chair
Springfield, Missouri
(417) 830-2337
Original Message:
Sent: 05-19-2023 09:50
From: Michael Smith
Subject: glycol piping layout
Hello:
Anyone out there have a minute to take a look at the attached glycol flow plan?
I am understanding the first in last out concept but what I'm curious about is where I have the heat exchanger plumbed in relation to all of the rest of the tanks.
Will this work good enough?
Is there a more ideal way to do this?
If so what makes a different route better?
Thank you,
Michael Smith
Head Brewer
Eel River Brewing Company
707-764-1772